I got a problem, My son-in-law and I installed a new fuse box, recontected everything up to the proper size circut breakers, everything works but the water heater(electric). It is on a 30 amp breaker, correct wire size, both black and white are hot(240v) but no hot water. We put a meter on the wires both have 120. Checked to make sure the are conected to the right braker and they are. Any ideas?
__________________
Crustiest of the OLD COOTS "Donating mirrors for years to help the Liberal/Socialist find their collective rear-ends, because both hands doesn't seem to be working. Veitnam 61-65:KIA 1864 66:KIA 5008 67:KIA 9378 68:KIA 14594 69:KIA 9414 70:KIA 4221 71:KIA 1380 72:KIA 300 Afghanistan2001-2008 KIA 585 2009-2012 KIA 1465 and counting Davros 1 Much abliged Massachusetts |
06-22-2004, 06:33 PM | #2 |
Apophis
Join Date: July 29, 2003
Location: The Underdark cavern of Zagreb
Age: 37
Posts: 4,679
|
Maybe a new heater? Check if it isn't a heater that demnds to be grounded or something.
__________________
MAKE LOVE, NOT SPAM! |
06-22-2004, 06:46 PM | #3 |
Fzoul Chembryl
Join Date: August 30, 2001
Location: somewhere
Age: 54
Posts: 1,785
|
I'm assuming the heater runs on 240V. A total of three wires in the power line to the house. 120VAC, 120VAC that is 180 degrees out of phase with the other, and neutral. The house also has an earth ground wire for safety hooked up to grounding rods or underground water pipes. On a 240V appliance you use both 120V hot wires for power. On a 120VAC appliance you use one of the two 120V hot wires and the neutral for power. Put the multimeter across the two hot wires at the heater hookup and you should have 240V AC. The neutral wire should not be hooked up to anything on a 240V appliance except possibly the ground. The earth ground should be hooked up to the ground connection. A 240VAC reading means you've got power. If you've got power to the heater, but it's not working, then the heater has to be busted. The amperage of the breaker will only be a problem if it blows, which it shouldn't.
__________________
Master Barbsman and wielder of the razor wit!<br /><br />There are dark angels among us. They present themselves in shining raiment but there is, in their hearts, the blackness of the abyss. |
06-22-2004, 09:04 PM | #4 |
Ironworks Moderator
Join Date: March 1, 2001
Location: Midlands, South Carolina
Age: 48
Posts: 14,759
|
Dude! Can you tell me how to set in ground wires for my house? The circuit box was replaced within the last 10 years from what I have been told, but only the new built-on room contains grounding. I want if nothing else, my PC grounded. I currently have it running from a battery and a seperate surge suppressor for the things like the printer.
[ 06-22-2004, 09:06 PM: Message edited by: Larry_OHF ]
__________________
|
06-22-2004, 09:33 PM | #5 | |
Ninja Storm Shadow
Join Date: March 27, 2001
Location: Northport,Alabama, USA
Age: 62
Posts: 3,577
|
Quote:
I've got a GE breaker box and I didn't know if the breaker could be only for 120v, though it's a 30amp breaker with 2 poles. This is driving me upthe wall cold showers in the morning aren't fun.
__________________
Crustiest of the OLD COOTS "Donating mirrors for years to help the Liberal/Socialist find their collective rear-ends, because both hands doesn't seem to be working. Veitnam 61-65:KIA 1864 66:KIA 5008 67:KIA 9378 68:KIA 14594 69:KIA 9414 70:KIA 4221 71:KIA 1380 72:KIA 300 Afghanistan2001-2008 KIA 585 2009-2012 KIA 1465 and counting Davros 1 Much abliged Massachusetts |
|
06-22-2004, 10:13 PM | #6 | |
Xanathar Thieves Guild
Join Date: January 8, 2001
Location: Charlotte,NC
Age: 60
Posts: 4,570
|
Quote:
[ 06-22-2004, 10:13 PM: Message edited by: Lord of Alcohol ]
__________________
No |
|
06-23-2004, 11:24 AM | #7 |
Ninja Storm Shadow
Join Date: March 27, 2001
Location: Northport,Alabama, USA
Age: 62
Posts: 3,577
|
It turned out to be that little space saver "wish I was a breaker", it had a pole broken I replaced it with a full size real man breaker and everything is working now.
__________________
Crustiest of the OLD COOTS "Donating mirrors for years to help the Liberal/Socialist find their collective rear-ends, because both hands doesn't seem to be working. Veitnam 61-65:KIA 1864 66:KIA 5008 67:KIA 9378 68:KIA 14594 69:KIA 9414 70:KIA 4221 71:KIA 1380 72:KIA 300 Afghanistan2001-2008 KIA 585 2009-2012 KIA 1465 and counting Davros 1 Much abliged Massachusetts |